A Freon 22 air conditioning under standard operating conditions of 35°C condensing
and 5°C evaporating temperatures. The volume flow rate entering the compressor is 23.72
L/s. Determine the refrigerating capacity if the refrigerating effect is 164 kJ/kg. From the table
for R22 the specific volume at the compressor entrance is 40.46 L/kg.